      Some of the storage cages in our NSW strata building (with sprinklers) are packed to overflowing.

      There has been concern from a resident that this may pose a fire risk.

      I have been unable to find any information online.

      Is anyone able to point me in the direction of any relevant fire regulations?

      Thank you very much

       

    Viewing 1 replies (of 1 total)
    • Author
      Replies
    • #64483 Reply
      Boronia
      Flatchatter

        Information available here:

        AS2118.1 1999 Clause 5.4.8 – Clear space below sprinklers

        Except as provided in Clauses 11.1.3.4(b) and 11.1.3.6(d) a clear space not less than 500 mm shall always be maintained below the level of the sprinkler deflectors throughout the room. For high piled combustible stock, clearance not less than 1m shall be provided. Roof trusses shall at all times be accessible to water discharged from the sprinklers.

        https://www.civilfire.com.au/fire-sprinklers/

      Viewing 1 replies (of 1 total)
      Reply To: Do we need fire sprinklers for storage cages?
      PLEASE ... If your property is not in NSW, mention its location (state). Don't identify companies or individuals by name. Don't mention or promote your company or services. Keep acronyms and initials to a minimum. Please, don’t use “quote” unless there is a specific point to which you wish to refer, then highlight (define) that specific passage before you click on "quote". Otherwise just use reply. THANKS.